    A/C line freezing up

    Noticed the temperature inside our home was not meeting up with thermostat setting and that air flow seemed low. Went outside and the lines running out of the outside A/C unit were frozen over leading into the house. Changed the filter and shut off the inside unit with the exception of the fan. Seemed to do the trick as the lines warmed back up.

    Woke up the morning and the lines are frozen over again. Shut off the inside unit again but any other ideas on what's wrong and how I can fix it? Being a holiday weekend, I can't call an A/C guy and not get charged an arm and a leg.

  2. #2
    asshat Sparky slams and goes hard. Sparky slams and goes hard. Sparky slams and goes hard. Sparky slams and goes hard. Sparky slams and goes hard. Sparky slams and goes hard. Sparky slams and goes hard. Sparky slams and goes hard. Sparky slams and goes hard. Sparky slams and goes hard. Sparky slams and goes hard. Sparky's Avatar
    Join Date
    Aug 2008
    Location
    Wally World Dad
    Posts
    3,277
    Frozen line means low flow on low side, which usually means lack of refrigerant.

  3. #3
    Cowboys and Texans fan ! tx 3 putt might be a clever chap. or know the right people. know what i mean, nudge nudge? tx 3 putt might be a clever chap. or know the right people. know what i mean, nudge nudge? tx 3 putt might be a clever chap. or know the right people. know what i mean, nudge nudge? tx 3 putt might be a clever chap. or know the right people. know what i mean, nudge nudge? tx 3 putt might be a clever chap. or know the right people. know what i mean, nudge nudge? tx 3 putt might be a clever chap. or know the right people. know what i mean, nudge nudge? tx 3 putt might be a clever chap. or know the right people. know what i mean, nudge nudge? tx 3 putt might be a clever chap. or know the right people. know what i mean, nudge nudge? tx 3 putt might be a clever chap. or know the right people. know what i mean, nudge nudge? tx 3 putt might be a clever chap. or know the right people. know what i mean, nudge nudge? tx 3 putt might be a clever chap. or know the right people. know what i mean, nudge nudge? tx 3 putt's Avatar
    Join Date
    Nov 2007
    Location
    Charlie's Bait Camp
    Posts
    49,492
    Quote Originally Posted by Sparky View Post
    Frozen line means low flow on low side, which usually means lack of refrigerant.

    which means a leak that has to be fixed

  4. #4
    fucktard John Blutarsky is probably perfectly normal.  Probably. Maybe. Who cares? John Blutarsky is probably perfectly normal.  Probably. Maybe. Who cares? John Blutarsky is probably perfectly normal.  Probably. Maybe. Who cares? John Blutarsky is probably perfectly normal.  Probably. Maybe. Who cares?
    Join Date
    Apr 2010
    Posts
    16
    Since you have already replaced your filter and eliminated that it could be low on refrigerant, a bad blower motor or a sticking compressor contactor. Can you feel air blowing when it is not frozen? Does the outdoor unit continue to run when you shut it off at the thermostat?

  5. #5
    asshat mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost's Avatar
    Join Date
    Dec 2007
    Location
    Hanging with the dumbfuckery crew
    Posts
    52,838
    Quote Originally Posted by John Blutarsky View Post
    Since you have already replaced your filter and eliminated that it could be low on refrigerant, a bad blower motor or a sticking compressor contactor. Can you feel air blowing when it is not frozen? Does the outdoor unit continue to run when you shut it off at the thermostat?
    Yes to feeling air blowing and it's still cold air. It just isn't blowing that hard. No to the outdoor unit continuing to run. It shuts off and the line thaws. I had to shut it off this morning because of more ice but it hasn't frozen over since then. Pretty sure the blower motor was changed out this time last year. Stuff like this always seems to happen to us on a holiday weekend. Last year, I think it went out during July 4th.

  6. #6
    fucktard John Blutarsky is probably perfectly normal.  Probably. Maybe. Who cares? John Blutarsky is probably perfectly normal.  Probably. Maybe. Who cares? John Blutarsky is probably perfectly normal.  Probably. Maybe. Who cares? John Blutarsky is probably perfectly normal.  Probably. Maybe. Who cares?
    Join Date
    Apr 2010
    Posts
    16
    Quote Originally Posted by mdmost View Post
    Yes to feeling air blowing and it's still cold air. It just isn't blowing that hard. No to the outdoor unit continuing to run. It shuts off and the line thaws. I had to shut it off this morning because of more ice but it hasn't frozen over since then. Pretty sure the blower motor was changed out this time last year. Stuff like this always seems to happen to us on a holiday weekend. Last year, I think it went out during July 4th.
    It is either low on refrigerant or the evaporator coil is dirty causing the air flow to be restricted. If you have a thermometer laying around check the return air temp and the supply air temp. You want to have 17-20 degrees differential. Less than that it is refrigerant. More than that is a dirty evap coil.

  7. #7
    asshat bluto Shaggy Gold Club bluto Shaggy Gold Club bluto Shaggy Gold Club bluto Shaggy Gold Club bluto Shaggy Gold Club bluto Shaggy Gold Club bluto Shaggy Gold Club bluto Shaggy Gold Club bluto Shaggy Gold Club bluto Shaggy Gold Club bluto Shaggy Gold Club
    Join Date
    Mar 2008
    Posts
    12,525
    lived in one of those massive apt complexes on riverside during college, went an entire summer w/ both my inside and outside ac lines freezing up. was a f'n bitch and of course the maintenance folks didn't know $#@!/didn't care so it was never fixed. pisses me off just thinking back to it.

  8. #8
    asshat Texas_Rocks Shaggy Gold Club Texas_Rocks Shaggy Gold Club Texas_Rocks Shaggy Gold Club Texas_Rocks Shaggy Gold Club Texas_Rocks Shaggy Gold Club Texas_Rocks Shaggy Gold Club Texas_Rocks Shaggy Gold Club Texas_Rocks Shaggy Gold Club Texas_Rocks Shaggy Gold Club Texas_Rocks Shaggy Gold Club Texas_Rocks Shaggy Gold Club Texas_Rocks's Avatar
    Join Date
    Dec 2008
    Location
    Valhöll Weed Patch
    Posts
    10,143
    Quote Originally Posted by John Blutarsky View Post
    It is either low on refrigerant or the evaporator coil is dirty causing the air flow to be restricted. If you have a thermometer laying around check the return air temp and the supply air temp. You want to have 17-20 degrees differential. Less than that it is refrigerant. More than that is a dirty evap coil.
    Listen to this guy! There is a very good chance that a clogged evaporator coil is the cause of your particular problem.

  9. #9
    Is the evaporator coil on the inside freezing up? That happens when you're low on freon and it will impede air flow (but the air will be cool). As a temporary fix you can turn on the inside fan (without the outside condenser) and after a couple of hours the evaporator will thaw out.

  10. #10
    asshat mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost's Avatar
    Join Date
    Dec 2007
    Location
    Hanging with the dumbfuckery crew
    Posts
    52,838
    Quote Originally Posted by hornalum View Post
    Is the evaporator coil on the inside freezing up? That happens when you're low on freon and it will impede air flow (but the air will be cool). As a temporary fix you can turn on the inside fan (without the outside condenser) and after a couple of hours the evaporator will thaw out.

    When I turned the inside unit to fan the first time, there was water dripping inside the unit so I think the coil was freezing up on the inside. It hasn't frozen up since yesterday. My primary concern now is why it isn't shutting off when it hits the desired temperature. Got a call into my service guy but he won't get it till tomorrow.

  11. #11
    asshat zzzz is probably pretty witty. or good at photoshop. or porn. zzzz is probably pretty witty. or good at photoshop. or porn. zzzz is probably pretty witty. or good at photoshop. or porn. zzzz is probably pretty witty. or good at photoshop. or porn. zzzz is probably pretty witty. or good at photoshop. or porn. zzzz is probably pretty witty. or good at photoshop. or porn. zzzz is probably pretty witty. or good at photoshop. or porn. zzzz is probably pretty witty. or good at photoshop. or porn. zzzz is probably pretty witty. or good at photoshop. or porn. zzzz is probably pretty witty. or good at photoshop. or porn. zzzz is probably pretty witty. or good at photoshop. or porn. zzzz's Avatar
    Join Date
    Feb 2008
    Posts
    11,582
    Your house wouldn't happen to be 5000 feet under the sea, would it?

  12. #12
    Be sure its thawed out when the service guy gets there or he won't be able to do much.

  13. #13
    Can someone recommend an a/c company in Katy? I need mine checked out.

  14. #14
    asshat mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost GORN mdmost's Avatar
    Join Date
    Dec 2007
    Location
    Hanging with the dumbfuckery crew
    Posts
    52,838
    It's cooling just fine now. Hasn't frozen up since yesterday morning. So maybe it was just the dirty air filter. I have two longhair cats so they might be the culprits. I still may have them come out and test it.

  15. #15
    asshat Swam4Texas Shaggy Gold Club Swam4Texas Shaggy Gold Club Swam4Texas Shaggy Gold Club Swam4Texas Shaggy Gold Club Swam4Texas Shaggy Gold Club Swam4Texas Shaggy Gold Club Swam4Texas Shaggy Gold Club Swam4Texas Shaggy Gold Club Swam4Texas Shaggy Gold Club Swam4Texas Shaggy Gold Club Swam4Texas Shaggy Gold Club Swam4Texas's Avatar
    Join Date
    Aug 2008
    Location
    Cedar Park/Corpus Christi
    Posts
    13,723
    Check and see if you're getting a steady flow of condensation from the evaporator coil. The dirty filter may have led to a clog.

+ Reply to Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Home .. Advertise .. ShaggyShop .. PanchoChat
Football .. Basketball .. Baseball .. Other Sports .. RC Didn't Offer .. Gamboool
Varsity .. Hole in the Wall .. PCL .. Einstein's .. Nasty's .. GM Steakhouse .. NSAA
Bada Bing .. Can you help me with this? .. Shagslist .. Cloak Room .. Classics .. Bellmont